Generator Power and Lathe

Joined
Mar 17, 2006
Messages
213
Likes
96
Location
Canton, Connecticut
I'm one of the 50% of CT residents without power, and currently (no pun) running the house with a portable generator. I don't run too much in the way of power consumption (fridge, freezer, computer and TV mostly). Just wondering if there is any risk to the motor on my Grizzly G0800 by using power from the generator. The motor is 220V/10A/3hp, so I think the wattage draw would be about 2200W. The generator puts out 7000W. I just don't know if there is something different about the power from the generator vs that from the utility lines, which could adversely affect the motor. Any electrical engineers out there? Thanks.
 
Joined
Mar 7, 2019
Messages
145
Likes
80
Location
Victoria, Texas
No difference in power. As long as the generator isn’t overloaded, everything will work fine. The generator has a breaker for protection as well. I’ve seen lathes run on generators without any issues.
 
Joined
Aug 14, 2009
Messages
2,030
Likes
1,119
Location
Peoria, Illinois
No trouble with the motor but I would be concerned about the VFD. How clean of power do you get with your generator? Is it an inverter generator? I wouldn't run my machines on a cheap traditional generator, but I'm cautious that way.
 
Joined
Apr 18, 2009
Messages
145
Likes
64
Ed, you could raise the question with the manufacturer of the lathe inverter. I agree that the motor shouldn't be a problem. My brother has lived with a 5 or 10KW generator for 60 years. 2 houses, 2 refrigerators, 2 chest freezers and a 3/4 hp pressure pump. Depending on the load, the pressure pump could drag the line voltage below 90 volts while it cycled on. Early TV's were the only appliance that tended to have a shorter life.
 
Joined
Sep 13, 2014
Messages
22
Likes
14
Location
Ontario, Canada
Lots of power outages here. We have a generator for the house and shop and one for the stable. Wouldn’t consider running either of my lathes because of VFDs. I even turn off the wifi router and wireless receiver. Generator power is too spiky for some electronics. Motors no problem.
 
Joined
Nov 26, 2009
Messages
787
Likes
717
Location
Rockingham, Virginia
The sine wave is incorrect for the VFD with a portable generator. I explored this back a few years ago, and I also have the G0800 & two other lathes. Not worth risking an electronic issue that fries the VFD. This info was passed on to me by an electrical engineer. Maybe Bill will chime in with some info.
 

Dennis J Gooding

Beta Tester
Beta Tester
Joined
Apr 10, 2010
Messages
824
Likes
732
Location
Grants Pass, Oregon
I am an electrical engineer and while I have not looked at the waveform of my emergency generator output, I can't see any reason why there should be any spikeiness. The generator is a classical AC device with a rotating magnetic field interacting with coils of wire and should produce an essentially perfect sinewave output. Spikeiness is usually is associated with waveform choppers used in voltage converters or VFD devices.
 
Joined
Mar 17, 2006
Messages
213
Likes
96
Location
Canton, Connecticut
Thanks for all the feedback. Based upon a couple of the replies, I decided to wait it out, and not risk doing damage to the VFD. The power was estimated to be out for 7 - 10 days. Before I turned the generator on this morning, I threw the main breaker and to my surprise, I'm back on line. At some point, I'll see if I can get more info from the manufacturer of the VFD.
 

Dennis J Gooding

Beta Tester
Beta Tester
Joined
Apr 10, 2010
Messages
824
Likes
732
Location
Grants Pass, Oregon
I am an electrical engineer and while I have not looked at the waveform of my emergency generator output, I can't see any reason why there should be any spikeiness. The generator is a classical AC device with a rotating magnetic field interacting with coils of wire and should produce an essentially perfect sinewave output. Spikeiness is usually is associated with waveform choppers used in voltage converters or VFD devices.

I am referring here to motor-generator emergency power systems. Units based on using an inverter to produce AC power from batteries or solar sources are a different story. Maybe some respondents are not making that distinction.
 
Joined
Jan 22, 2009
Messages
441
Likes
678
Location
Crossville, TN
All generators are not created equally. I would have no concern running my Powermatic (with VFD controller) on an inverter-generator which puts out a true sine wave, and I’ve run various electronics successfully on. These are higher cost generators, typically with sound insulation etc.

I would not risk running sensitive electronics (including VFD controller) on a contractor style generator. These are cheaper, usually open frame, where the engine runs at constant rpm regardless of the load. Output of these are not as clean as inverter-generators.
 

Roger Wiegand

Beta Tester
Joined
Nov 27, 2018
Messages
789
Likes
914
Location
Wayland, MA
Website
www.carouselorgan.com
OK, I'm confused, doesn't a generator need to run at constant rpm to produce power at a constant 60hz? Obviously I'm not an electrical engineer! Is there electronic wizardry that adjusts the frequency coming out of generators? It seems like in old (steam powered) generators I'm more familiar with the designers went to a lot of trouble to be able to hold speed constant while delivering more or less power to the generator.

Given the declining state of our power grid and advancing age and dependence on electrically powered devices we recently installed a whole house Generac 15 kVA system. The guys who sold it to us assured me that it was fine to use all of our electronic devices while running on the generator; indeed we've had two outages in the three weeks since it was installed and everything kept running just fine. Is what they told me not true, and are we courting disaster?


All generators are not created equally. I would have no concern running my Powermatic (with VFD controller) on an inverter-generator which puts out a true sine wave, and I’ve run various electronics successfully on. These are higher cost generators, typically with sound insulation etc.

I would not risk running sensitive electronics (including VFD controller) on a contractor style generator. These are cheaper, usually open frame, where the engine runs at constant rpm regardless of the load. Output of these are not as clean as inverter-generators.
 

Dennis J Gooding

Beta Tester
Beta Tester
Joined
Apr 10, 2010
Messages
824
Likes
732
Location
Grants Pass, Oregon
OK, I'm confused, doesn't a generator need to run at constant rpm to produce power at a constant 60hz? Obviously I'm not an electrical engineer! Is there electronic wizardry that adjusts the frequency coming out of generators? It seems like in old (steam powered) generators I'm more familiar with the designers went to a lot of trouble to be able to hold speed constant while delivering more or less power to the generator.

Given the declining state of our power grid and advancing age and dependence on electrically powered devices we recently installed a whole house Generac 15 kVA system. The guys who sold it to us assured me that it was fine to use all of our electronic devices while running on the generator; indeed we've had two outages in the three weeks since it was installed and everything kept running just fine. Is what they told me not true, and are we courting disaster?

Roger, like you, I have a whole-house generator, propane-powered in my case. For this application, it is considered important to maintain a frequency very close to 60 Hertz so that clocks and timers do not drift much during outages. The frequency for any given unit, is determined by engine speed which is controlled by a sensitive governor system. In the case of a two-pole generator, like mine, the engine speed is maintained at 3600 RPM, regardless of load up to the maximum capacity of the generator. (A four-pole generator would run at 1800 RPM.) I have no data on contractor portable motor generators, but I would expect that accurate speed regulation is not considered important. However, even with these, I would not expect to find voltage spikes.
 
Joined
Jan 22, 2009
Messages
441
Likes
678
Location
Crossville, TN
I can’t speak for power quality on whole- house generators, but would assume they’re good.

The OP asked about a portable generator. The standard contractor grade portable runs at constant speed, but when loaded down it will vary enough that the wave output differs significantly from a pure sine wave. Those are the ones I would not use with sensitive electronics.

Portable inverter-generators actually convert the generated AC voltage to DC and then back to 60Hz AC so they produce a much higher quality sine wave output, typically spec’d at 1-3% of perfect sine wave I believe. These are the portable generators play well with sensitive electronics.
 
Joined
Jul 19, 2018
Messages
1,686
Likes
2,077
Location
Ponsford, MN
The VFD has a rectifier on the single phase input and it then constructs a 3 phase sine wave at the voltage and frequency requested example 50% speed would require an out put voltage of 120 V 30 Hz 3 phase. The VFD uses pulse width modulation, which is rapid on off switching to approximate that sine wave, therefore the VFD usually protects it self due to the DC bus, as it sends electrical noise back on the line.
 