For the Delta S1 inverter, there are three inputs required for the inverter to operate. A Run command, A Direction command and A Speed reference command. There are 3 LED’s on the left side of the display for the RUN, FWD and REV command. With the E-stop button out, Run Position, you should have the RUN LED. Push the button in, E-Stop position and the RUN LED should go out.
With the E-Stop in RUN position and the RUN LED displayed, change the position of the FWD and REV switch and the corresponding direction LED’s should change status. There is an alfa numeric display on the control face that can be programmed to indicate several things. I believe the default is F for frequency input to the Inverter. If you have the display starting with an “F”, slowly rotate the speed control potentiometer from minimum “0” display to maximum about “135” and back to “0”. The display numbers should increment and decrement smoothly and without any noticeable skips. Yes, the Inverter is programmed to overdrive the motor to about 135 Hz. The inverter will not operate w/o the “F” speed reference input even if the e-stop is working, in the RUN position and you have a FWD or REV signal.
If any of the above inputs are missing or the speed reference is unstable, those inputs need to be corrected. I suggest you run this test first to try to pinpoint the problem before you poke around in the wiring and/or blow out switches or the potentiometer with compressed air. It should take less than 30 seconds to perform once you have done it.