Power 220v Lathe with a Buck Boost Transformer

Joined
Jul 1, 2021
Messages
17
Likes
7
Location
Park Ridge, Il
Hello
For a number of reasons getting 220v to where I need it for a lathe is going to be difficult. Has anyone used a Buck Boost Transformer to power a 220v lathe from a 110v plug? Any pro/cons?

Thanks
 
Joined
Aug 26, 2006
Messages
656
Likes
558
Location
Hampton Roads Virginia
Had to look it up, but according to the second paragraph at this link,
110 to 220 is too big a jump...
 

Roger Wiegand

Beta Tester
Joined
Nov 27, 2018
Messages
794
Likes
932
Location
Wayland, MA
Website
www.carouselorgan.com
How big is the motor on your lathe? You can certainly use a transformer (though not what is sold as a buck/boost) but if you have a 2+ hp motor your 120V circuit may too small to support it anyway unless it is a dedicated 20A circuit. If it is the latter you can just swap the breaker to turn it into a dedicated 240V line. With a reasonable guess on power factor and efficiency a 2 hp motor draws just over 15 A at 120V, so probably shouldn't share a 20A line with anything else. Given the several hundred dollar cost of that size transformer it is probably reasonable to go to at least a little difficulty to pull a new circuit.

Check the motor plate on your lathe, many motors are dual voltage and can be rewired to run on either 120/240V. The primary advantage of 240 is that you can use smaller gauge wire to feed the circuit.
 
Joined
Jul 26, 2016
Messages
2,326
Likes
1,105
Location
Nebraska
You might research a rotophase type apparatus which are usually used to create 3-phase power from single phase power.
One of these companies may make a 120V to 220V version.

A long S/O cord with a 220V cord end and a 220V breaker on the other end would be my quickest solution to powering a lathe.
 